The Bacnet protocol is within the PCOWEB, not on the controller.

To configure the PCOWEB they will have to:

1) On screen "Ge01" (Found in Service --> e. BMS config.) Set:
- the BMS Protocol: CAREL
- Baud rate: 19200
- Address: 1

2) Press "Esc" till you return to the Home screen
3) Press "the alarm bell" and "Enter" keys to gether for few seconds till the system information screen appears.
4) Scroll down to "OTHER INFORMATION", then press the "Enter" Key
5) Scroll down to "PCOWEB/NET CONFIG" then press the "Enter" Key
6) Select the "PCOWEB Settings" then press the "Enter" Key
7) In this section of the menu they will be able to set the IP address, the Subnet mask, default gateway and the Bacnet ident. At the end of the options they will need to save to any changes.

Hope this helps.