To connect via Modbus RS485 using the built in port on the controller, you will need to connect on J25, the navigate on the main menu of the controller to: Service-->BMS config.--> Type password (probably 0000) --> then scroll down to screen Ge01a (BMS2 protocol).

Here, please make sure that the settings are: 
Protocol: MODBUS
Boud rate: 19200 (or change to suit BMS requirements)
Address: Unique address in the network.

That's all you need to do.
The Modbus has a fixed Stop Bits = 1 and Parity: NONE