Home Forums Technical Support How does the Fireman Override work on the FLSTDmMAHUE?

Viewing 1 post (of 1 total)
  • Author
    Posts
  • 5ms 5ms
    Keymaster
    Post count: 38

    On receipt of a smoke clearance signal from the Fire Alarm panel, the AHU shall close the inlet damper to 100%  and the Exhaust dampers to 100% open. The Extract Fan will then run at 100%. This alarm is a manual reset. To reset this alarm press the Alarm bell twice to acknowledge and reset, then In “Service-> Manual management”(screen Gg01) change the Extract fan from “99” to “AUTO”.

Viewing 1 post (of 1 total)
  • The forum ‘Technical Support’ is closed to new topics and replies.